消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

竖向金属风管穿楼板(只穿一层),不做土建井道可以吗?

竖向金属风管穿楼板(只穿一层),不做土建井道可以吗?

Madapple | 2024-06-21 15:49
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 8

黄-江西省景德镇市 2024-06-23 22:32 00 [回复]举报

烟规4.4.8第二款 竖向设置的排烟管道应设置在独立的管道井内,排烟管道的耐火极限不应低于0.5小时;

4.4.11 设置排烟管道的管道井应采用耐火极限不小于1小时的隔墙与相邻区域分隔。

PS:也就是说独立的竖向金属排烟风管的耐火极限不应低于1.5小时,还要用不然材料保温。

潘天坤 2024-06-24 00:28 00 [回复]举报

个人觉得,如果竖向穿一整层应该设置管道井或者设置类似管道井耐火极限做法(井道耐火极限为1小时),同时注意井道或者类似做法内的排烟管道应保证0.5小时耐火极限

 烟规GB51251规定:竖向设置的排烟管道应设置在独立的管道井内,此时排烟管道的耐火极限不应低于0.50h 

 如果只是局部穿一小段,做个防火保护也就算了,一整层建议遵照规范要求执行

上述为根据国家规范的个人理解,有些地区技术文明可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

Madapple   回复: 潘天坤2024-06-24 09:59

明白了,谢谢!风管从下穿至上:如下层的吊顶,穿一次楼板,穿到设备转换层,该层内还有正压送风机,该层是否建议仍旧按独立管井考虑?

0    0 [回复]举报

潘天坤   回复: Madapple2024-06-24 14:31

是否考虑做个类似管井的做法?如果穿越不是很多,局部一小区域应该问题不大,主要看区域内专家们的意见

0    0 [回复]举报

Madapple   回复: 潘天坤2024-06-24 17:06

还有一个问题请教一下:吊顶中的风管,穿楼板处,是否需要设土建风道夹层呢?

0    0 [回复]举报

潘天坤   回复: Madapple2024-06-25 14:35

从吊顶内穿一个楼板,楼板之外的竖向距离有多少?如果大于3米,个人觉得需要设置

0    0 [回复]举报

Madapple   回复: 潘天坤2024-06-26 14:31

好的,明白了,即形成风井的概念了,就要设置,谢谢。

0    0 [回复]举报

LHH2737 2024-06-27 16:55 00 [回复]举报

要设置,但是土建井道可以占天不占地

关闭

关闭

手机APP下载