食品加工厂洁净室排烟口形式可以用单层百叶吗

如图,一个排烟阀带两个排烟口可以吗?有老师提出需要用板式排烟口,有依据吗



消防网友62117 | 2023-12-07 11:01
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

GANSTER 2023-12-08 08:49 00 [回复]举报

板式排烟口主要防止室外空气倒灌,影响车间洁净度。

mshm 2023-12-16 17:54 00 [回复]举报

没啥问题,排烟阀平时关闭,两侧气流是不流通状态。

潘天坤 2024-06-18 13:29 00 [回复]举报

考虑板式排烟口可能是防止漏风考虑

洁净规范有这个要求,食品工业洁净规范没有提到这方面内容 

洁净室施工及验收规范 GB50591-2010第12.2.4条规定:排烟口应安装板式排烟口,不应漏风