消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

压力开关启泵

大型化工企业采用官网压降信号启泵,由于厂区大,装置分散,现有火灾自动报警控制器多,约一百多台,自动喷水灭火系统的压力开无法自动启泵,请问火灾自动报警系统的消火栓、自动喷水灭火系统联动启动设计要求是否适用于大型?化工企业,如要执行,大型化工企业该如何执行

ruihua | 2024-09-12 15:19
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

磊中 2024-09-14 11:22 00 [回复]举报

都是适用的,但石油化工企业有自己的相关规范《石油化工企业防火设计标准》

具体执行时,是要参考两个规范的

《石油化工企业防火设计标准》8.5.1条文中稳高压消防给水系统,平时采用稳压设施维持管网的消防水压力,但不能满足消防时的用水量要求。当发生火灾启动消防水设施时,管网系统压力下降,靠管网压力联锁自动启动消防水泵,

所以消防泵是靠供水管道上的低压压力开关启泵是可以的,但是自动喷水灭火系统应该有报警阀组上的压力开关联锁启泵的

ruihua   回复: 磊中2025-02-16 10:01

启泵可以靠报警阀组压力开关联动启动,若要实现直接启泵(联锁)困难较大,企业内有7百多套阀组,若均连接反而会导致系统不平稳,石化规之规定了启泵靠管网压降信号启动,其他均未作出规定,所以导致实施困难,是否还有更好的解决方法?

0    0 [回复]举报

关闭

关闭

手机APP下载