消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

湿式报警阀压力开关 完工时 发现连接了2根线 说是一去一回 连接到消防控制室操作台,还有2根线是未连接状态,问下此种方式(2根未连接)是否可以,如果不可以要连接哪里?依据哪个规范?

湿式报警阀压力开关  完工时 发现连接了2根线  说是一去一回 连接到消防控制室操作台,还有2根线是未连接状态,问下此种方式(2根未连接)是否可以,如果不可以要连接哪里?依据哪个规范?

一红到底 | 2024-08-06 13:35
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 5

资源网小助理 2024-08-06 14:53 10 [回复]举报

另外两根接水泵控制柜启泵

消防网友68723 2024-08-06 14:55 00 [回复]举报

11.0.1 湿式系统、干式系统应由消防水泵出水干管上设置的压力开关、高位消防水箱出水管上的流量开关和报警阀组压力开关直接自动启动消防水泵

资源网小助理 2024-08-06 14:57 00 [回复]举报

11.0.1 湿式系统、干式系统应由消防水泵出水干管上设置的压力开关、高位消防水箱出水管上的流量开关和报警阀组压力开关直接自动启动消防水泵。

半曰闲 2024-08-06 16:11 00 [回复]举报

火灾自动报警系统设计规范 GB50116-2013 

4.2.1 湿式系统和干式系统的联动控制设计,应符合下列规定:    1 联动控制方式,应由湿式报警阀压力开关的动作信号作为触发信号,直接控制启动喷淋消防泵,联动控制不应受消防联动控制器处于自动或手动状态影响。        3 水流指示器、信号阀、压力开关、喷淋消防泵的启动和停止的动作信号应反馈至消防联动控制器


所以,4根线都要接。

acy 2024-08-09 08:03 10 [回复]举报

一组接控制柜直启端子(带自锁),另一组接反馈模块,反馈模块是现场,信号反馈给消控室主机。

关闭

关闭

手机APP下载