消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

旅馆建筑室内消火栓设置要求

石老师,旅馆建筑是否需要设置室内消火栓是否需要同时执行通规第8.1.7 (5、6条)吗?

5 建筑体积大于5000m³的下列单、多层建筑:车站、码头、机场的候车(船、机)建筑,展览、商店、旅馆和医疗建筑,老年人照料设施,档案馆,图书馆;
6 建筑高度大于15m或建筑体积大于10000m³的办公建筑、教学建筑及其他单、多层民用建筑;

安泰 | 2024-07-11 22:54
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

LHH2737 2024-07-12 09:32 00 [回复]举报

对于旅馆,体积大于5000m3,建筑高度大于15m,这两点满足任一点就需要设置室内消火栓系统

秘密1 2024-07-12 11:22 00 [回复]举报

只需满足体积大于5000立方米的要求,因为第五条也是单多层建筑,第六条的其他单多层民用建筑指除第五条之外的。

安泰   回复: 秘密12024-07-12 21:20

谢谢

0    0 [回复]举报

关闭

关闭

手机APP下载