关于喷嘴的控制系统

在实际工程中,面积区域较大的1个防护区,安装了8个喷嘴,请问若某处角落着火了,需要启动全部喷嘴淹没全室吗?还是只需要启动局部喷嘴释放灭火即可

zzyzy | 2024-06-03 16:01
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

黄辉 2024-06-04 08:18 00 [回复]举报

气体灭火系统的喷嘴都是开式的,系统启动后,同一防护区的喷头全部喷灭火剂灭火。

七氟丙烷、IG541等气体灭火系统是全淹没应用方式,灭火时需要防护区达到灭火浓度才能灭火,所以不能只在发生火灾的部位局部喷灭火剂灭火。

zzyzy   回复: 黄辉2024-06-04 17:57

非常感谢您的回答!那如果是很大的一个空间呢?印象中看到过一个文献写着,如果防护区面积过大超过了规范的最大面积限值,可以假想成多个防护区进行设计,那在这种情况下是不是在某处角落着火了,只有着火区域附近的那块喷嘴释放灭火呢

0    0 [回复]举报

黄辉   回复: zzyzy2024-06-05 08:16

七氟丙烷、IG541只能采用全淹没灭火系统,如果空间很大,可能就不太适合做七氟丙烷、IG541气体灭火系统。


气体灭火系统设计规范 GB50370-2005对防护区有面积、体积限制。

3.2.4 防护区划分应符合下列规定:

    1 防护区宜以单个封闭空间划分;同一区间的吊顶层和地板下需同时保护时,可合为一个防护区;

    2 采用管网灭火系统时,一个防护区的面积不宜大于800m²,且容积不宜大于3600m³;

    3 采用预制灭火系统时,一个防护区的面积不宜大于500m²,且容积不宜大于1600m³。


如果时大空间的局部部位需要做气体灭火,可以考虑采用二氧化碳局部应用灭火系统(二氧化碳时唯一可以做局部应用的气体灭火系统)。前提时要考虑安全,二氧化碳不能用于经常有人停留的场所。

0    0 [回复]举报