变配电室上方水喷淋系统是否需要

变配室上方有没有不能安装喷淋的法规,低压配规范内仅说明了配电室内不得有水管,

看书想睡觉 | 2021-03-08 09:44
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 15

窝窝头 2021-03-08 11:34 30 [回复]举报

配电室属于规范要求的不宜设置喷水灭火系统的,设置的话,要也是设气体灭火系统。

ps:设计个喷淋,设计师脑子歪掉了吧,电力公司也不会让你搞这么大。

看书想睡觉   回复: 窝窝头2021-03-10 09:23

现在就是有个漏洞,他吊顶用的普通矿棉板水管布在吊顶上方

0    0 [回复]举报

窝窝头   回复: 看书想睡觉2021-03-13 09:00

如果没人知道估计没事,一旦漏水发生事故,出图纸的设计院就逃不了被追责,不要去挑战规范

0    0 [回复]举报

即刻   回复: 看书想睡觉2023-01-15 16:37

严禁这种做法。可以倒个混凝土顶。

0    0 [回复]举报

小马 2021-03-10 11:32 00 [回复]举报

给谁管道都不得穿越变配电房的= =  肯定不能设置喷头,让设计重新改图吧

凡爸   回复: 小马2021-04-21 22:11

我们这高压配电室和网络机房里用的高压细水雾灭火系统,真要是喷放了,不短路或者连电吗?

0    0 [回复]举报

小马   回复: 凡爸2021-06-24 15:04

对于细水雾这块,我确实不了解,我们的高压配电室和网络机房全都是七氟丙烷气体灭火,不过如果你们的图纸经过住建局审批那应该也是没有问题的,我也就见过一次细水雾的运用,是一个类似电视上看到的那种交通局监控中心那样的。

0    0 [回复]举报

钱到位,人干废   回复: 小马2023-12-28 17:58

理论上细水雾应该是可以的,但是我见到的一般都是气体或者干粉

1    0 [回复]举报

消防网友75620 2021-03-11 15:51 00 [回复]举报

8.3.8 下列场所应设置自动灭火系统,并宜采用水喷雾灭火系统:
    1 单台容量在40MV·A及以上的厂矿企业油浸变压器,单台容量在90MV·A及以上的电厂油浸变压器,单台容量在125MV·A及以上的独立变电站油浸变压器;
    2 飞机发动机试验台的试车部位;
    3 充可燃油并设置在高层民用建筑内的高压电容器和多油开关室。
    注:设置在室内的油浸变压器、充可燃油的高压电容器和多油开关室,可采用细水雾灭火系统。

窝窝头   回复: 消防网友756202021-03-13 08:58

胆子这么大的设计院没几个

0    0 [回复]举报

曹顺凯 2022-01-29 20:10 00 [回复]举报

可气体

蓝天枫 2022-02-22 16:50 00 [回复]举报

高压细水雾绝对没问题

wangge1986n 2022-05-09 15:39 00 [回复]举报

配电房一般设置柜式或管网式七氟丙烷气体灭火系统。

新雪无痕 2023-04-25 06:19 00 [回复]举报

配电室内应没气休灭火设施

大树119 2023-07-10 21:36 00 [回复]举报

E类火灾用水灭火,这怎么玩?