办公一楼大堂是设置防烟还是设置排烟

建筑概况:建筑层数,地上8层,地下1层,一层大堂,净高7.8米,大堂面积150㎡左右,大堂又是作为首层楼梯直通室外的扩大前室,甲方想只设置防烟,不设置排烟,这样是可以的吗,感谢

请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

南明离火 2024-04-24 17:10 00 [回复]举报

只设置防烟 是当做扩大前室用,扩大前室的话 ,众所周知 不允许挪作他用

安洪全 2024-04-24 17:24 00 [回复]举报

个人理解

把大厅当作前室来看的话,设防烟。

排烟也可以设自然排烟窗,在外立面的顶部

消防网友68723 2024-04-25 10:11 00 [回复]举报

 

3 公共建筑内建筑面积大于100m²且经常有人停留的地上房间; 应设排烟设施

香.香 2024-05-10 13:27 00 [回复]举报

既然是扩大前室那扩大前室与大厅之间是有防火分隔措施的,扩大前室只需要防烟就可以了。还有一点确认一下大厅是不是扩大前室,满不满足扩大前室的设置要求。

潘天坤 2024-06-19 19:08 00 [回复]举报

相关规范没有关于“首层扩大的封闭楼梯间或防烟楼梯间前室“的防排烟设施的描述

不少地区的技术文件有作出要求,例如:可开启外窗的有效面积不应小于扩大前室地面面积的3%,且不应小于3平方米。当扩大前室面积大于 100㎡、空间高度跨越两层且兼作建筑大堂功能时,宜按大堂排烟的相关要求设置自然排烟或机械排烟设施

建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑