消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

柜式预制灭火系统在一个防护区最多设计个数?

在检查中,对柜式预制灭火系统在一个防护区设计个数不清楚?

消防网友66891 | 2021-02-25 15:41
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0

回答 | 2

消防打工人 2021-02-26 14:40 00 [回复]举报

《气体灭火系统设计规范 GB50370-2005》3.1.14 一个防护区设置的预制灭火系统,其装置数量不宜超过10台。

邦哥 2021-04-05 16:10 00 [回复]举报

防护区内所有预制灭火系统需要同时启动,误差不超过2秒。如果预制系统多了,这条执行起来的确困难。所以,规范要求预制系统最好不超过10台。

关闭

关闭

手机APP下载