消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

在烟规中,系统中任一排烟阀或排烟口开启时,排烟风机、补风机自动启动;是否指的是联锁启动呢?

5.2.2 排烟风机、补风机的控制方式应符合下列规定:

1 现场手动启动;   

2 火灾自动报警系统自动启动;   

3 消防控制室手动启动;   

4 系统中任一排烟阀或排烟口开启时,排烟风机、补风机自动启动;   

5 排烟防火阀在280℃时应自行关闭,并应连锁关闭排烟风机和补风机。


5.2.2 本条对排烟风机及其补风机的控制方式做出了更明确的规定,要求系统风机除就地启动和火灾报警系统联动启动外,还应具有消防控制室内直接控制启动和系统中任一排烟阀(口)开启后联动启动,目的是确保排烟系统不受其他因素的影响,提高系统的可靠性。本条为强制性条文,必须严格执行。


本条规范和条文解释如上,是否可以理解为:联动控制器和风机控制柜都调为“自动”状态时才可以实现呢?还是说要实现风口联锁开启风机的功能?

尤里奥洛夫 | 2023-12-08 23:00
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 9

同同不同 2023-12-09 10:01 00 [回复]举报

联动

阳明心 2023-12-11 11:20 00 [回复]举报

按照文字理解,只要实现系统中任一排烟阀或排烟口开启时,排烟风机、补风机自动启动功能,连锁或联动都可以。

尤里奥洛夫   回复: 阳明心2023-12-11 15:05

联动的要求肯定会低一些,毕竟不需要线路直接连接啊

0    0 [回复]举报

阳明心   回复: 尤里奥洛夫2023-12-11 16:07

对啊,我理解联动的可靠性不如连锁



0    0 [回复]举报

我的是昵称 2023-12-11 15:11 00 [回复]举报

你没有搞明白连锁和联动的意思。联动你可以理解为需要联动控制器逻辑判断。连锁就像连锁反应一样,是不需要控制器,这边有动作那边就启动。就像水泵连锁启泵,压力低于低压压力开关设定值就直接启泵。而风口开风机是需要联动控制器控制启动的,所以是联动启动。

尤里奥洛夫   回复: 我的是昵称2023-12-11 15:35

你没有看过石峥嵘写的连锁和联动控制解读,上面写的是风口需要连锁控制风机开启,但是规范里写的是联动。

0    0 [回复]举报

我的是昵称   回复: 尤里奥洛夫2023-12-11 15:45

那要是你去执业,你是按规范来还是按石峥嵘写的解读来?你认为设计院会按石峥嵘写的解读来设计?很明显就是按规范执行的。

0    0 [回复]举报

尤里奥洛夫   回复: 我的是昵称2023-12-15 17:00

我们就是执业单位,现在主管部门的要求不一样,所以导致有些项目可以按规范做,有些项目就一定按联锁来实现。

0    0 [回复]举报

潘天坤 2024-06-18 13:52 00 [回复]举报

规范里没有明确受不受主机状态影响

图集为通过总线联动开启

建议按照设计要求执行

关闭

关闭

手机APP下载