消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

试验消火栓动压过高如何处理?

 26层住宅屋顶试验消火栓动压为0.6Mpa,需设减压装置吗?

与笑同行 | 2023-07-05 09:42
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

安洪全 2023-07-05 10:06 00 [回复]举报

宜设置减压装置,避免压力过大造成操作人员受伤。

可采用减压型消火栓。


消防给水及消火栓系统技术规范 GB50974-2014

7.4.12 室内消火栓栓口压力和消防水枪充实水柱,应符合下列规定:    

1 消火栓栓口动压力不应大于0.50MPa;当大于0.70MPa时必须设置减压装置;


条文说明:

1 室内消火栓一般配置直流水枪,水枪反作用力如果超过200N,一名消防队员难以掌握进行扑救。DN65消火栓口水压如大于0.50MPa,水枪反作用力将超过220N,故本款提出消火栓口动压不应大于0.50MPa,如果栓口压力大于0.70MPa,水枪反作用力将大于350N,两名消防队员也难以掌握进行灭火。因此,消火栓栓口水压若大于0.70MPa必须采取减压措施,一般采用减压阀、减压稳压消火栓、减压孔板等。

同同不同 2023-07-05 13:19 00 [回复]举报

是什么样子的住宅这么牛?顶层0.6的话,负一层管网承受1.6以上的压力,危险很大,没跟设计沟通么,满足13m、0.35是否可行?

关闭

关闭

手机APP下载