消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

室内消火栓

根据消规:建筑高度大于15m或体积大于10000m3的办公建筑、教学建筑和其他单、多层民用建筑。需要设置室内消火栓,请问建筑高度是按照建筑高度计算到女儿墙还是按照建筑的消防高度计算呢

月卉 | 2023-05-20 14:51
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 8

无名之辈 2023-05-20 17:23 00 [回复]举报

女儿墙的高度不计算在建筑的消防高度里啊

月卉   回复: 无名之辈2023-05-23 09:30

是呀,但是按照新规分为建筑高度和建筑消防高度,但是防火规范没更新,两个高度不一样,就涉及到要不要上消火栓

0    0 [回复]举报

月卉   回复: 无名之辈2023-05-23 09:31

是的,但是就是水专业的消火栓问题,要是按照建筑高度那就是超过15m,就要上消火栓;按照建筑消防高度,就没到15m,就不需要上消火栓

0    0 [回复]举报

鱼剑客 2023-05-20 22:52 00 [回复]举报

公共建筑的室外地面设计高度到屋面面板高度,女儿墙不计入建筑高度

月卉   回复: 鱼剑客2023-05-23 09:33

所以公共建筑的建筑高度和建筑消防高度还是一样的?只计算到平屋面吗

0    0 [回复]举报

安洪全 2023-05-22 11:37 00 [回复]举报

建筑设计防火规范 GB50016-2014(2018年版)

A.0.1 建筑高度的计算应符合下列规定:    

1 建筑屋面为坡屋面时,建筑高度应为建筑室外设计地面至其檐口与屋脊的平均高度。    

2 建筑屋面为平屋面(包括有女儿墙的平屋面)时,建筑高度应为建筑室外设计地面至其屋面面层的高度。    

3 同一座建筑有多种形式的屋面时,建筑高度应按上述方法分别计算后,取其中最大值。    

4 对于台阶式地坪,当位于不同高程地坪上的同一建筑之间有防火墙分隔,各自有符合规范规定的安全出口,且可沿建筑的两个长边设置贯通式或尽头式消防车道时,可分别计算各自的建筑高度。否则,应按其中建筑高度最大者确定该建筑的建筑高度。    

5 局部突出屋顶的瞭望塔、冷却塔、水箱间、微波天线间或设施、电梯机房、排风和排烟机房以及楼梯出口小间等辅助用房占屋面面积不大于1/4者,可不计入建筑高度。    

6 对于住宅建筑,设置在底部且室内高度不大于2.2m的自行车库、储藏室、敞开空间,室内外高差或建筑的地下或半地下室的顶板面高出室外设计地面的高度不大于1.5m的部分,可不计入建筑高度。

A.0.2 建筑层数应按建筑的自然层数计算,下列空间可不计入建筑层数:    

1 室内顶板面高出室外设计地面的高度不大于1.5m的地下或半地下室;    

2 设置在建筑底部且室内高度不大于2.2m的自行车库、储藏室、敞开空间;    

3 建筑屋顶上突出的局部设备用房、出屋面的楼梯间等。

无名之辈 2023-05-23 14:13 00 [回复]举报

以建规为准

月卉   回复: 无名之辈2023-07-31 18:20

好的 谢谢

0    0 [回复]举报

关闭

关闭

手机APP下载