大型商业综合体店铺内消防应急照明及疏散指示系统接线问题

土建消防验收已经通过,现招商店铺施工进场,想问下,店铺应急照明灯具接线是接到集中电源回路上,还是让接到商铺进线后店铺配电箱让他们自己留单独回路???店铺自己接会出现无法集中控制,接到公区应急回路,每天闭店断电应急照明灯具常亮店铺内的电费无法收取。试问具体该怎么接线

猫熊学消防 | 2022-07-27 17:45
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

周家斌 2022-07-28 08:31 10 [回复]举报

与原来土建一消验收合格时候一个系统,不要改变原控制模式。应急灯具的电费是公共(物业)的。

猫熊学消防   回复: 周家斌2022-07-29 14:45

那就得用统一的灯具理,我看现实中大型商业综合体很少有这样做的

0    0 [回复]举报

南明离火   回复: 猫熊学消防2022-07-29 17:23

那是因为太小的商铺没办施工许可证没有验收,乱做,走正规验收流程的主力店要按设计图纸接入系统

0    0 [回复]举报

消防网友73006 2022-07-28 14:39 10 [回复]举报

肯定接入物业原有土建消防系统

李勤 2022-07-30 10:39 10 [回复]举报

商铺改建保持原有设计。像之前写字楼处于节能考虑采用两火一零(消防专用线路),不影响日常闭店后断电、节能。