喷头不小心被碰破了,怎么办

当消防自喷系统中,喷头不小心被碰破了,该怎么处理

荣荣 | 2022-07-18 16:52
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

周家斌 2022-07-18 17:15 30 [回复]举报

关闭所属的主管上的信号蝶阀,打开放水阀,更换喷头,打开信号蝶阀,末端末端放水阀排空气,恢复系统待工作状态。

消防黄河 2022-07-18 20:43 40 [回复]举报

报备单位消防管理人,请维保或有资质人员更换维修,检查恢复。紧急时先关闭该喷头所在配水管或配水干管上便于操作的阀门,若喷头所属配水管有试水阀亦同时打开排水,减少水渍损失,用备用喷头进行更换,放水排气恢复系统。

荣荣   回复: 消防黄河2022-07-20 12:51

谢了!

1    0 [回复]举报

hujun 2022-07-18 22:48 30 [回复]举报

通知同事去做关信号阀开末端,自己准备好换的衣服和洗发水沐浴露,先洗为敬。