消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

11.0.17 消防水泵的双电源切换应符合下列规定: 1 双路电源自动切换时间不应大于2s;

11.0.17 消防水泵的双电源切换应符合下列规定: 6 消防末端配电箱应设置在消防水泵房、消防电梯机房、消防控制室和各防火分区的配电小间内;各防火分区内的防排烟风机、消防排水泵、防火卷帘等可分别由配电小间内的双电源切换箱放射式、树干式供电。


问:10000V消防泵电机如何实现末端双电源切换?谢谢


zjs | 2022-07-15 11:16
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

zjs 2022-07-15 11:27 00 [回复]举报

 消防用电设备的供电应在配电线路的最末一级配电装置处设置双电源自动切换装置(检查要点是看两个回路是不是来自不同的电源或不同段母线,回路是否完全独立,末端双电源切换装置是否可靠)。当发生火灾时,仍应保证消防用电。10000V消防泵如何实现末端切换?????

关闭

关闭

手机APP下载