病房门的开启方向

《综合医院建筑设计规范》GB51039-2014第 5.5.5条要求:病房门应直接开向走道。 是病房门的开启方向开向走道吗? 现在好多的病房都是开向病房里面的。

念_BOvL | 2022-05-30 11:28
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 8

充楞装傻 2022-05-30 11:44 10 [回复]举报

不是开启方向,这是门的位置; 如果都朝外开的话~疏散通道就被堵完了

念_BOvL   回复: 充楞装傻2022-05-30 15:37

这个有相应的规范或者解释么?


0    0 [回复]举报

周家斌 2022-05-30 14:27 10 [回复]举报

参考石老师:疏散走道-20问! https://b.1190119.com/article-337.htm

念_BOvL   回复: 周家斌2022-05-30 15:36

这个图解解决的是怎么样避免对疏散走廊净宽的影响。。。我现在需要知道的是病房的门是不是就一定要对外开启,现在的医院病房我看都是往病房里面开,而不是往走廊开。我研究的是开启方向,不是怎样避免对疏散走廊净宽的影响。

0    0 [回复]举报

周家斌   回复: 念_BOvL2022-05-30 17:02

是要求门的设置通向走道,不是门扇开启方向的意思。向外、向内开执行建规6.4.11

1    0 [回复]举报

wsxiebo 2022-05-31 11:01 00 [回复]举报

病房门应直接开向走道与病房门向疏散走道开启是两个意思;病房门应直接开向走的意思重于门出去就是走道,开启方向应参考《建规》6.4.11。

吴俊 2022-06-01 10:19 00 [回复]举报

住院楼病房门应直接开向通道,注意不是开门方向;

开门方向按照建规疏散门开启方向直行  和病房的面积和疏散人数有关系

消防黄河 2022-06-30 15:02 00 [回复]举报

医院规该条款指的是门的位置,人数不超过60人且每个门平均疏散人数不超过30人时开启方向不限。