消防水泵启动后需要稳压泵停泵,这个功能是怎么实现的

消防水泵启动后需要稳压泵停泵,这个功能是怎么实现的

王召峰 | 2021-10-09 22:20
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

都叫我老张 2021-10-10 10:17 00 [回复]举报

稳压泵在自动状态,当管网水压低于稳压泵启泵设定值时,稳压泵自动启动。

消防水泵启动后,管网水压逐渐上升,上升至稳压泵停泵设定值时,稳压泵自动停泵。

杨江峰 2021-10-10 15:18 00 [回复]举报

消防水泵是消防水泵,稳压泵是稳压泵,不明白你这个意思

消防打工人 2021-10-10 21:22 00 [回复]举报

稳压泵是通过电接点压力表来控制启停的,消防泵启动后管网压力上升达到电接点压力表上限时控制稳压泵停止。