剪刀梯和消防电梯的合用前室是可以用自然通风吗?规范是说宜用机械加压送风系统


岁月辉煌 | 2021-09-07 23:57
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

刘丽波 2021-09-10 21:33 00 [回复]举报

剪刀梯的一个前室与消防电梯的前室合用时,条件允许时可以采用自然通风;三合一前室必须设置机械加压送风方式。

岁月辉煌   回复: 刘丽波2021-09-11 15:12

规范哪条三室合一的前室是要求必须设置机械加压送风系统的?

我在条文说明那看到的是宜设置机械加压送风系统,而且我觉得现在的自然通风要比机械加压送风系统要好得多。

0    0 [回复]举报

岁月辉煌   回复: 岁月辉煌2021-09-12 21:04

谢谢老师的答复,但我个人觉得规范没有用强条来要求,而且条文说明那还用了个宜字,是否有退一步的可能呢?

0    0 [回复]举报

刘丽波   回复: 岁月辉煌2021-09-13 10:27

一般对于新建工程没有这个宜的说法。可以看一下各地的防排烟问题汇总,只有湖南地区有点放宽,其余都要求机械加压。

1    0 [回复]举报

刘丽波 2021-09-11 19:42 00 [回复]举报

《烟规》3.1.3