消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

人员密集型场所外保温应采用a型材料?这个是强条嘛

假如,我要开个酒吧,酒吧在商铺二楼,假如这个商铺外保温是b1 的,并且商铺是2010年建好的,或者15年建好的,整栋楼都是b1的外保温,我是不是必须把我这层的外保温改了?

陈施工 | 2021-06-22 01:37
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 1

一条咸大鱼 2021-06-22 08:57 10 [回复]举报

建筑设计防火规范 GB50016-2014(2018年版) >6.7.4 设置人员密集场所的建筑,其外墙外保温材料的燃烧性能应为A级。该条为强制执行的条款。


另外,该建筑性质功能的变更视面积和地方要求,应按照“三同时”要求执行,按消防从严的角度来考虑,建议改造外保温。

关闭

关闭

手机APP下载