山林古建筑布置火灾报警系统,现场条件不满足线路暗埋敷设,请问还有其他什么合适的敷设方式吗?

山林古建筑布置火灾报警系统,现场条件不满足线路暗埋敷设,请问还有其他什么合适的敷设方式吗?

请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

潘天坤 2025-04-15 09:53 00 [回复]举报

没有暗敷条件的话,也可以采用穿金属管、可挠(金属)电气导管、金属封闭线槽保护,采用矿物绝缘类不燃性电缆可直接明敷,不过要考虑明敷时消防配电线路的要求


山林古建筑如果有条件可以按照火灾自动报警系统相关规范执行,如果条件受限可以参考文物建筑防火设计规范、古建筑修建工程施工及验收规范等等,也可以看下地区是否有技术文件支持


上述言论为根据国家规范的个人理解和交流探讨,不一定正确,也不能作为依据 有些地区技术文件可能有特别规定,建议楼主多与区域内设计、审查及验收等专家交流,具体以他们意见为准


EHS专家-DL 2025-04-15 11:49 10 [回复]举报

耐火金属管、防火线槽、无线信号传输技术(无需物理线路连接)等。结合《文物建筑防火设计导则》的消防总体布局要求,优先选择对建筑本体干预最小的方式‌。

消防资源网 2025-04-15 12:01 10 [回复]举报

文物建筑防火设计规范 WW/T0125-2025


8.2.7 由于线路敷设、维护困难或文物保护需要不允许敷设线路的文物建筑或场所,可采用无线火灾自动报警系统或独立式火灾探测报警器无线组网系统。