消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

地下车库通过住宅楼梯疏散时,通道上的门应采用什么防火门

地下车库通过住宅楼梯疏散时,车库通往住宅楼梯间需经过一段通道,车库与此通道的分隔要采用甲级防火门,这个规范上很明确,但是当通道两侧有其他房间,如工具间、储藏间、水井、电井等,这些门需要采用什么防火门

石老先生 | 2025-03-27 16:09
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

EHS专家-DL 2025-03-28 09:07 00 [回复]举报

  1. 设备用房(水井、电井等)
    通道内的水井、电井等设备间门应采用‌丙级防火门‌。此类房间火灾风险较低,且规范未要求其与疏散通道之间必须采用更高等级的防火门‌。

  2. 储藏间、工具间等可燃物存放房间
    若房间存放可燃物(如工具间、储藏间),其通向疏散通道的门应至少采用‌乙级防火门‌,以减缓火势向疏散路径蔓延的速度‌。

  3. 防火分区边界门
    若通道两侧房间属于其他防火分区,分隔门需根据防火分区要求选择防火等级(通常为甲级或乙级)。例如,设备用房防火分区与车库防火分区之间的门需采用‌甲级防火门。‌‌


vicher 2025-04-09 14:41 00 [回复]举报

该区域是否属于避难走道?避难走道需满足《建筑设计防火规范》第6.4.14条的要求。

关闭

关闭

手机APP下载