请问不同的防烟分区可以公用排烟风管吗?

耐烧王 | 2025-02-24 17:36
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

冼锟 2025-02-24 19:49 10 [回复]举报

可以的

耐烧王   回复: 冼锟2025-03-07 16:32

感谢

0    0 [回复]举报

潘天坤 2025-02-24 19:53 10 [回复]举报

同一防火分区内,沿横向设置,管径符合要求的话,可以共用主管,支管得单独设置,同时应避免管道穿越防火分区且不允许在同层几个防火分区共用一套机械排烟系统,以防止火灾经排烟管道和防火阀蔓延至着火区域外的其他防火分区,保证防火分区的完整性和防火分隔的可靠性


机械排烟系统应按照不同防火分区独立设置,要求系统的排烟风机 、 排烟管道和排烟口均应独立,但消防电源可以共用



耐烧王   回复: 潘天坤2025-03-07 16:32

非常感谢