楼顶消火栓静压

各位老师:关于高层楼顶消火栓静压的标准值有什么规范(大楼采取是楼顶消防水箱稳压)?

红门铠甲 | 2025-02-21 11:07
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

亲亲子衿 2025-02-21 11:39 10 [回复]举报

消防给水及消火栓系统技术规范 GB50974-2014

5.2.2 高位消防水箱的设置位置应高于其所服务的水灭火设施,且最低有效水位应满足水灭火设施最不利点处的静水压力,并应按下列规定确定:
1 一类高层公共建筑,不应低于0.10MPa,但当建筑高度超过100m时,不应低于0.15MPa;
2 高层住宅、二类高层公共建筑、多层公共建筑,不应低于0.07MPa,多层住宅不宜低于0.07MPa;
3 工业建筑不应低于0.10MPa,当建筑体积小于20000m³时,不宜低于0.07MPa;
4 自动喷水灭火系统等自动水灭火系统应根据喷头灭火需求压力确定,但最小不应小于0.10MPa;
5 当高位消防水箱不能满足本条第1款~第4 款的静压要求时,应设稳压泵。

小唐12321   回复: 亲亲子衿2025-02-21 14:59

设置稳压泵就不应低于0.15

0    0 [回复]举报

小当家   回复: 小唐123212025-02-26 16:09

设稳压泵,要>0.15MPa,不能=

0    0 [回复]举报