消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

工业厂房,一个建筑不同防火分区存在大面积内凹,如果在一面设置甲级防火门窗,这个距离可以不限吗?

建筑防火规3.4.7范要求同一座厂房内凹时宜大于相应的建筑距离,如果内凹一侧设置甲级防火门窗,这样可以距离不限吗?

消防网友77957 | 2024-11-30 16:26
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

云中飞翔 2024-12-01 20:42 10 [回复]举报

可以这样考虑,规范规定,厂房内相邻防火分区之间防火墙上可以设置不可开启或火灾时能自行关闭的甲级防火窗。如果是内凹的两面墙其中一面为防火墙(前提是火灾时可自行关闭的防火窗),两个防火分区距离即可不限。

jinyanwu 2024-12-02 09:04 10 [回复]举报

建规这样规定:

设置甲级防火门窗的规定如下(建规3.4.1条注3):

距离不限的规定如下(建规3.4.1条注2):

消防网友77957   回复: jinyanwu2024-12-02 10:28

谢谢老师

0    0 [回复]举报

关闭

关闭

手机APP下载