二氧化碳灭火器称重

请问各位专家二氧化碳灭火器应多久称重一次,是每月、半年还是其他?

sky | 2024-11-12 14:06
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

陈泽平 2024-11-12 14:56 00 [回复]举报

《手提式灭火器第1部分:性能和结构要求》GB4351.1-2005

6.7.1 由灭火剂蒸气压力驱动的灭火器和二氧化碳贮气瓶应用称重法检验泄漏量。灭火器的年泄漏量不应大于灭火器额定充装量的5%或50g(取两者的小值)。贮气瓶的年泄漏量不应大于额定充装量的5%或7g(取两者的小值)。


《建筑灭火器配置验收及检查规范》GB50444-2008
5.2.1 灭火器的配置、外观等应按附录C的要求每月进行一次检查。
5.2.2 下列场所配置的灭火器,应按附录C的要求每半月进行一次检查。
1 候车(机、船)室、歌舞娱乐放映游艺等人员密集的公共场所;
2 堆场、罐区、石油化工装置区、加油站、锅炉房、地下室等场所。

附录C 建筑灭火器检查内容、要求及记录

sky   回复: 陈泽平2024-11-12 16:45

感谢回复,对于车间来说是要每月称重一次是吗?

0    0 [回复]举报

jinyanwu 2024-11-18 14:30 00 [回复]举报

根据GB50444-2008,二氧化碳灭火器称重周期应根据现场情况确定;有的一个月,有的半个月;